Old-Biscuit wrote:
If using the 30A to 50A adapter doesn't cause problems for your DAD then he needs to check the 50A receptacle he is plugging into isn't one for 'welder'....no neutral
โAug-19-2013 06:51 PM
Cecilt wrote:
...I can use the dogbone to take my 50 amp to 30 amp when at a 30amp only pedestal and...All else will work fine?
โAug-19-2013 05:59 PM
โAug-19-2013 05:09 PM
โAug-19-2013 04:19 PM
wbwood wrote:
I would go ahead and get it with the 2nd a/c. Better to have it and not need it than not to have it and wish you did.
โAug-19-2013 01:48 PM
โAug-19-2013 01:44 PM
MitchF150 wrote:Old-Biscuit wrote:MitchF150 wrote:
If you are plugged into a 30a you won't be able to use both AC's at the same time. For the 50a setup, each AC unit is wired to a separate leg of the 50a plug. For the 30a, you only have one hot leg, thus one AC with power to it...
Mitch
If you plug the 30A in and then test each hot on the 50A end, both will have voltage.
30A to 50A adapter feeds both hots on the 50A.
Trying to run both A/C's at same time is a problem due to only having 30 amps total available
My mistake... My dad has 50a on his rig and when he plugs into 50a, he blows the system, with 240v going thru it... It's mucked up on the 50a side for sure, but when he uses the adapter to plug into 30a, it's fine.
I first thought that was because the other leg was not hot... Thinking about it more now, the 30a is only 120v no matter what, so both legs can be hot with 120v as stated...
Dad just does not use 50a anymore... He's had it checked out, but no one has been able to resolve it and he does not need 50a anyway...
Thanks for the clarification.
Mitch